Can I use an 220v extension cord to use the 220v dryer plug for charging my RAV4 PHEV?
If the breaker is 40 amps, the wiring to the outlet should be 8 gauge Romex. The breaker, wiring, and outlet should be safe to carry up to 32 amps continuous, so if your EVSE is pulling 26~28, you are a bit under that and within the safe upper limit. But here's a thought for you to consider: I assume you are in one of these utility districts: LADWP, SoCal Edison, or SDG&E (San Diego Gas and Electric). If your utility offers a special discount rate for EV charging, it probably applies between midnight to 06:00am, or maybe 11:00pm to 07:00am if they are generous. A totally discharged Rav4 Prime needs about 15.5 kW-hour to get back to 90.2% state of charge, which is the maximum. If your service is 240 volts, 15,500 watt hours at 240 volts = 64.5 amp-hours. If you get the discount rate for 6 hours a night, divide 64.5/6=10.76. What that means is that any charge rate above 10.76 amps at 240 volts will charge your car to "full" in 6 hours or less. Your EVSE probably supports charging at 16 amps (most of them do), or you can set 16 amps in the car's charge settings with the buttons on the steering wheel. 16 amps x 240 volts = 3840 watts. Divide 15,500 by 3840 and you get 4 hours (this will actually be closer to 5 hours because the charge rate slows down during the last 10% of the charge session). So if you set your charge rate to 16 amps, you get these benefits:my dryer, oven, and garage outlet (used for my charger) are all 40 amps.
The plugs and sockets are all rated 40 amps, house built in 1997 in So Cal, and that was the code at the time..
my charger maxes out at 26-28 amps....
I'm ok...
Assuming the house wiring was properly installed, there should be no danger of the wires overheating or catching fire because the circuit breaker will trip before that happens. The wires in socket are rated for a certain current and the circuit breaker will be safe to trip before it reaches that current.When a car charges at 6.6 kw vs 1.3 or 3.3 there is obviously more flow. more flow makes me think more heat. more heat destroys the washer outlet and wires (As it is not designed for heavy loads and long duty cycles). when wire casing fails due to heat it cracks off or catches fire. FIRE BAD!
When I charge on 120v with a 15amp fuse i get 11-12 amps, when i charge on a 20 amp fused circuit i get 16 amps. when i charge on a 240v (14/50)outlet i get 32 amps. More AMPS, More Heat, Larger wire size.
Bottom line. If you can afford a Rav4 Prime. Get the correct stuff and do not be cheap. If my renter did something stupid like merging outlets, or hooking up a car charger to the laundry dryer... they would not be renting from me or anyone who asked for a reference.
The OP i believe got a new Rav4P, and maybe 21 on had an optional 6.6 KW onboard charger, and 22 on came with a 6.6KW. That is twice the capasity of the previous ones.
EV Outlets are designed for a higher duty cycle. If you look at your provided outlet it would say EV on the lower right side. look at the outlet and then again after a few months. Did the black plastic start to turn white? Look oxidized a bit? A clothes dryer may have the same rating, but how long does it actually hit the maximum amps? just like any appliance the start up takes more load and then quickly reduces to the running amps... maybe 1/2!? and for an hour. your car has a red line for rpms. does that mean you drive at redline for 6-10 hrs straight? Nope if you did it would not last a week. similar with current.Assuming the house wiring was properly installed, there should be no danger of the wires overheating or catching fire because the circuit breaker will trip before that happens. The wires in socket are rated for a certain current and the circuit breaker will be safe to trip before it reaches that current.
The real problem will be that the current you need to charge the car quickly will be more than what that circuit can provide.
As I mentioned in this thread we have a 50 amp circuit for our charger in our one car garage and a 100 amp circuit for the two-car garage.
I also have a 100 Amp subPanel for (2) 50 amp charging outlets. one for the wife's BMW and one for my prime.Assuming the house wiring was properly installed, there should be no danger of the wires overheating or catching fire because the circuit breaker will trip before that happens. The wires in socket are rated for a certain current and the circuit breaker will be safe to trip before it reaches that current.
The real problem will be that the current you need to charge the car quickly will be more than what that circuit can provide.
As I mentioned in this thread we have a 50 amp circuit for our charger in our one car garage and a 100 amp circuit for the two-car garage.
I also have a 2021 R4P SE. I recently discovered that my city has installed several ChargePoint chargers in public parking lots and the cost is zero (for the time being at least). So I stopped charging my car at home with my level 1 unit and use those public chargers whenever I am in the area, which is 4 or 5 days a week, usually for around 2 hours. They are level 2. The activity report on the ChargePoint app shows a gain of about 8 miles of range per hour of charging, but the car's odometer screen shows an increase in EV range of about 12 miles per hour.I have a 2021 R4P SE which means the fastest I can charge is on a 3rd party EVSE full charge - 4.5 hrs.
I tested the stock EVSE on 220V supply and a full charge took almost 6 hrs. (not sure how you charge in 5).
Later model R4Ps come with a faster charger (in car) so if supported by enough current capacity they can charge in 2-1/2 hrs on 220V.
Google search genius. You know that top bar where they have pictures and prices! I didn’t say it was a good deal. I was giving a range.Uhhh..... what?
an "ev outlet"?
used this 40 amp outlet since 1998, no it's not white, cracking, but when I plug in the 4 cylinder, 150 psi, 30 scfm compressor, it sparks, and after all these years, need to replace, getting worn...
sounds nuts..... please provide a link for the $200 socket ha ha!
ok, I did some research: on the hubble site it's $49..... look here: Hubbell Store
Uhh, if you want to buy one for $200 and think it's special, please contact me for purchase of a bridge... got one cheap...
it's the same one with a green stamp...perhaps it has some minor tweak....
whoever has quoted your one for $200, that person is ripping you off...
You started this, and had silly comments. Your very technical comment of the outlet having tweaks earned you the sparky name.Giving an absurd range is not helpful, and creating a stigma that you need a special EV socket is also not helpful.
I don't like to play, but I'm hear to learn and to be helpful, not so sure about you...
Don't need sealant, there is nothing wrong, especially with 24 years of wear on something not designed for lots of in and out...
also you clearly don't know anything about compressors, S stands for "standard" look it up
I already had a full ev, as stated.
So you are a person whose top goal is to not be opposed, vs trying to help and being thankful that you "accidentally" led people astray with poor knowledge and reading skills.
It is indeed a sticker with some tweeks, because is is only a couple of dollars more than the one without a sticker, did you fail basic econommics too?
Stop the personal comments, and read, and decide if you want to be helpful and respected, or just another guy with wild, unsupported opinions..
My comments are intended to be helpful and factual, your are speculative, uninformed, and somewhat ignorant.
This thread is about charging, not oil changes. Suggest you open a new thread with your specific questions.Anyone here care to share an opinion on Oil Change schedules?
perhaps I should have added a wink. 😉This thread is about charging, not oil changes. Suggest you open a new thread with your specific questions.
But I highly suggest you use the search function first to look up existing threads on oil changes, oil type, etc. There are many of them (perhaps too many). The topic has been hashed and rehashed so many times and people tend to get very argumentative. Then the moderators have to close down the thread.
You will probably find the answer to your questions by doing a search, rather than start a new thread.
I was looking, but could not easily find one.EV Outlets are designed for a higher duty cycle.
quick search on amazon yields this one as an example. There are lots of choices.I was looking, but could not easily find one.
Could you share a link for a nema 14-50 240v outlet that is specific for EV charging?
Thanks. It is interesting that for Leviton there appear to be 2 versions of this outlet: a standard EV one, and a weather-resistant EV one. Your link is to the standard one I think. Although the images are confusing.quick search on amazon yields this one as an example. There are lots of choices.
![]()
Amazon.com: Leviton 50 Amp EV Charging Receptacle/Outlet, Heavy Duty, 1450R, Black : Automotive
Buy Leviton 50 Amp EV Charging Receptacle/Outlet, Heavy Duty, 1450R, Black: Charging Station Accessories - Amazon.com ✓ FREE DELIVERY possible on eligible purchaseswww.amazon.com
quick search on amazon yields this one as an example. There are lots of choices.
![]()
Amazon.com: Leviton 50 Amp EV Charging Receptacle/Outlet, Heavy Duty, 1450R, Black : Automotive
Buy Leviton 50 Amp EV Charging Receptacle/Outlet, Heavy Duty, 1450R, Black: Charging Station Accessories - Amazon.com ✓ FREE DELIVERY possible on eligible purchaseswww.amazon.com
Maybe wait until you have a full EV and just monitor the plug you have now. Outside may be safer than inside. lots of heat sensing tricks: a couple times around the plug with electrical tape, and check to see if the tape released it's glue / wrinkled up. Is there any dark discoloration? or electrical smell from outlet box mid charge. unplug once every few months to check for cracking or plug getting loose in outlet.Thanks. It is interesting that for Leviton there appear to be 2 versions of this outlet: a standard EV one, and a weather-resistant EV one. Your link is to the standard one I think. Although the images are confusing.
So this gets me thinking. I had an electrician install a 14-50 outlet at the front of our house exclusively for EV charging. Looking at it, it appears to be a random "standard" 240v outlet, in a steel weather resistant housing. I do not not unplug it very often, less than once a year. We just charge a couple of PHEVs, no full EVs. Is it worth it for me to replace my standard 14-50 outlet with one of these EV weather resistant ones? All opinions welcome.
Check google for difference between Dryer outlet and EV outlet. there are a dryer outlets that also are only 30amp and should only be used in the 24amp charge setting. Your thoughts are not the same as the majority in the know. Designs dont need to be significant to be better. Just saying for those who might actually want to know what is best for charging at 32amps for a long duration.No reason to buy the one with the green logo in my opinion. As I stated, I plugged and unplugged mine many times over the years and it is only sort of worn now after 12 years of sharing that outlet with a high current air compressor, which has one hell of a surge current (starts immediately when plugged in) a point that person I blocked on this thread did not understand.
There cannot be a significant difference in design, since the costs are so close. It very well may be it is identical except for the green logo.